General => Beating a dead horse => Topic started by: bandito on August 17, 2014, 12:24:16 am
-
The GFI breaker has recently has been jumping lately. Whenever the heater kicks in a few minutes later the breaker jumps and one if the leads coming from the breaker gets hot and smokes a little. Here is a picture of the lead (http://i1065.photobucket.com/albums/u381/mazdawarrior/20140816_131944_zpse0bc93b5.jpg) (http://s1065.photobucket.com/user/mazdawarrior/media/20140816_131944_zpse0bc93b5.jpg.html). I tested the breaker with a volt meter. 117 volts from each hot lead to ground and 234 from hot lead to hot lead so it appears to be working properly. I checked all the wiring for shorts and no luck. I also poked around the wiring looking for one the may be hot which was not the case. I even pulled the filter figuring that maybe the pump was working to hard. Any ideas for trouble shooting?
-
So I replaced the breaker with a 40amp breaker as specified in the manual. Ran it for about 6 hours with no problems or any wires getting hot.
-
If you replaced it with a 40 amp breaker what size GFI breaker were you using before?